Did you know that the most common cause of defrost failure is a dirty air filter? Most service techs will sell you a new board and termination switch but most of the time it is not needed.
During defrost the heat pump switches into cooling mode to pump some heat out of the house to melt the ice on the outdoor coil. If the filter is clogged the heat needed to defrost cannot reach the indoor coil and most defrost board algorithms give up on defrost after 10 or 12 minutes so some of the ice remains and it gets worse with every failed defrost cycle. Check your air filter before you call for service.